AC CONDENSER UNIT, roof run-off

New postPosted: Fri Apr 10, 2009 10:45 am
by RICHARD TAN
Hi Jerry,

AC condenser unit under eaves, valley or kick out flashing. Is there a code or manufacturer guideline to prevent excessive rain water runoff into the ac condenser?

Re: AC CONDENSER UNIT, roof run-off

New postPosted: Fri Apr 10, 2009 1:25 pm
by Jerry Peck - Codeman
Hi Richard,

Yes, the code requires the mechanical equipment and appliances to be installed in accordance with their installation instructions and the installation instructions state not to install it under roof runoff.

The easy solution, then, is to install a 10 foot long piece of gutter centered above the condenser unit as that allows the roof runoff to be diverted to each side of the condenser unit.