Bill Kriegh wrote:There is a line of panels manufactured specifically for pass through applications (Cutler Hammer, I think. I need to find my correspondence.)
Hi Bill,
If you find that, would you please post it?
Panelboards are listed to UL Standard 67 and that standard does not test for pass through conductors.
When I contacted the customer service about this they indicated the only difference in the panels was that the breaker buss bar assembly is offset to one side to allow a straight wire feed for the pass through wire. No extra space is alloted for the purpose.
The problem is not the lack of extra space, but the lack of extra space provided specifically for that purpose. The reason is not fill as there is usually sufficient fill space to accommodate additional conductors, the main reason is "pass through current" in that current not originating in that enclosure at those breakers will add heat and temperature rise to the panel, and that zero pass through current is what is being tested.
Additionally, if they were to allow for pass through conductors, the secondary reason is that the space provided for those conductors would need to be isolated from the other conductors by a suitable (i.e., listed, labeled, and provided by the manufacturer of the panelboard and enclosure) grounded metal separator shield to make sure that the pass through conductors could not come in contact with conductors originating at the overcurrent devices (breakers) - one would not want to turn all breakers to 'off' only to have an energized pass through conductor accidentally contact and energize a conductor with its overcurrent protection in the 'off' position, both for worker safety from electrical shocks and for fire safety and overcurrent protection of the conductors.
Testing for pass through conductors would need to be established to establish the minimum conductor size and its maximum pass through current allowed, and, the maximum conductor size and the maximum pass through current allowed, and the full tests would need to be run with the newly established allowances. The listing and labeling would need to state the maximum number and size combinations of cables and the fully loaded current condition acceptable.
It's a lot more complicated than just 'is there enough space' and 'is there enough wire bending space'.