GFCI receptacles with a W

New postPosted: Fri May 15, 2009 8:29 am
by Bill Kriegh
From the UL White Book:
Weather-resistant Receptacles — Receptacles for use in wet and damp
locations in accordance with Article 406 of the NEC. Weather-resistant receptacles
are identified by the words ‘‘Weather Resistant’’ or the letters ‘‘WR’’
where they will be visible after installation with the cover plate secured as
intended.

Re: GFCI receptacles with a W

New postPosted: Fri May 15, 2009 9:04 am
by Jerry Peck - Codeman
Hi Bill,

Your post relates to this question: viewtopic.php?f=3&t=107

Thank you for that information.

I was not connecting the 'W' with the 'WR', although it now seems so obvious.

Again, thank you.

Re: GFCI receptacles with a W

New postPosted: Mon May 18, 2009 11:55 am
by Jerry Peck - Codeman
Just adding more information from the UL White Book in case it is needed.

- Receptacle-type GFCIs for use in wet and damp locations in accordance with Articles 406 of the NEC are identified by the words ‘‘Weather Resistant’’ or the letters ‘‘WR’’ where they will be visible after installation with the cover plate secured as intended.
- Weather-resistant receptacle-type GFCIs installed in wet locations are intended to be installed with an enclosure that is weatherproof, whether or not the attachment plug cap is inserted.